Snowdog wrote:

It appears to be a rigid copper wire wrapped in a mesh shielding..kind of
like a potato sack mesh...i don't think it's metal. There are only two
wires..no ground wire. I do understand your point about grounding from the
panel. I guess i will have to rerun a new wire.


I forget the NEMA designation for that, but it's basically the predicessor
to Romex. Putting a three-prong outlet on the end of that stuff is a big,
big code violation.

You may want to make sure the rest of the house isn't the same way. if it
is, you can legally keep three-prong outlets by using a GFI on each circuit.
(The GFIs will trip if there is substantial leakage, like there is with that
bass amp. That doesn't help you with the bass amp, though.) But you do
not want to have three-prong ungrounded outlets, if only because it probably
invalidates your insurance.

(I am assuming it _is_ a house... that stuff was never code for commercial
construction....)
--scott

--
"C'est un Nagra. C'est suisse, et tres, tres precis."
  #45   Report Post  
Scott Dorsey
 
Posts: n/a
Default

Snowdog wrote:

It appears to be a rigid copper wire wrapped in a mesh shielding..kind of
like a potato sack mesh...i don't think it's metal. There are only two
wires..no ground wire. I do understand your point about grounding from the
panel. I guess i will have to rerun a new wire.


I forget the NEMA designation for that, but it's basically the predicessor
to Romex. Putting a three-prong outlet on the end of that stuff is a big,
big code violation.

You may want to make sure the rest of the house isn't the same way. if it
is, you can legally keep three-prong outlets by using a GFI on each circuit.
(The GFIs will trip if there is substantial leakage, like there is with that
bass amp. That doesn't help you with the bass amp, though.) But you do
not want to have three-prong ungrounded outlets, if only because it probably
invalidates your insurance.

(I am assuming it _is_ a house... that stuff was never code for commercial
construction....)
--scott

--
"C'est un Nagra. C'est suisse, et tres, tres precis."


  #46   Report Post  
Scott Dorsey
 
Posts: n/a
Default

Snowdog wrote:

It appears to be a rigid copper wire wrapped in a mesh shielding..kind of
like a potato sack mesh...i don't think it's metal. There are only two
wires..no ground wire. I do understand your point about grounding from the
panel. I guess i will have to rerun a new wire.


I forget the NEMA designation for that, but it's basically the predicessor
to Romex. Putting a three-prong outlet on the end of that stuff is a big,
big code violation.

You may want to make sure the rest of the house isn't the same way. if it
is, you can legally keep three-prong outlets by using a GFI on each circuit.
(The GFIs will trip if there is substantial leakage, like there is with that
bass amp. That doesn't help you with the bass amp, though.) But you do
not want to have three-prong ungrounded outlets, if only because it probably
invalidates your insurance.

(I am assuming it _is_ a house... that stuff was never code for commercial
construction....)
--scott

--
"C'est un Nagra. C'est suisse, et tres, tres precis."
  #47   Report Post  
Pooh Bear
 
Posts: n/a
Default



Snowdog wrote:

I pulled the three prong outlet from the wall that the bass player plugs
into...and sure enough, there are only two wires connected to the plug.
There is no grounding wire. I do see a ground terminal on the outlet to add
a ground wire. House was built in '56.


Is that legal ?

Certainly wouldn't be in the UK.

Are ungrounded outlets common in the US ?


Graham

  #48   Report Post  
Pooh Bear
 
Posts: n/a
Default



Snowdog wrote:

I pulled the three prong outlet from the wall that the bass player plugs
into...and sure enough, there are only two wires connected to the plug.
There is no grounding wire. I do see a ground terminal on the outlet to add
a ground wire. House was built in '56.


Is that legal ?

Certainly wouldn't be in the UK.

Are ungrounded outlets common in the US ?


Graham

  #49   Report Post  
Pooh Bear
 
Posts: n/a
Default



Snowdog wrote:

I pulled the three prong outlet from the wall that the bass player plugs
into...and sure enough, there are only two wires connected to the plug.
There is no grounding wire. I do see a ground terminal on the outlet to add
a ground wire. House was built in '56.


Is that legal ?

Certainly wouldn't be in the UK.

Are ungrounded outlets common in the US ?


Graham

  #50   Report Post  
Logan Shaw
 
Posts: n/a
Default

George wrote:

From what I understand the two prong outlets were grounded through the
armored jacket or conduit
so if a ground path is in place through one of thes methods then simply
bond the green screw of the three hole edison connector to the metal job
box


I think the OP said the wire was two conductor enclosed in a mesh
that did not appear to be metal. So, apparently there really is
no separate ground.

- Logan


  #51   Report Post  
Logan Shaw
 
Posts: n/a
Default

George wrote:

From what I understand the two prong outlets were grounded through the
armored jacket or conduit
so if a ground path is in place through one of thes methods then simply
bond the green screw of the three hole edison connector to the metal job
box


I think the OP said the wire was two conductor enclosed in a mesh
that did not appear to be metal. So, apparently there really is
no separate ground.

- Logan
  #52   Report Post  
Logan Shaw
 
Posts: n/a
Default

George wrote:

From what I understand the two prong outlets were grounded through the
armored jacket or conduit
so if a ground path is in place through one of thes methods then simply
bond the green screw of the three hole edison connector to the metal job
box


I think the OP said the wire was two conductor enclosed in a mesh
that did not appear to be metal. So, apparently there really is
no separate ground.

- Logan
  #53   Report Post  
Logan Shaw
 
Posts: n/a
Default

Pooh Bear wrote:
Snowdog wrote:
There is no grounding wire. I do see a ground terminal on the outlet to add
a ground wire. House was built in '56.


Is that legal ?

Certainly wouldn't be in the UK.

Are ungrounded outlets common in the US ?


On older houses (say, 1960s or before, or maybe it's 1950s or before),
yes they are common, but not on newer construction.

Keep in mind that, in the US, virtually everything is "new construction"
by UK standards. We do have the occasional house that is over 100 years
old, but it's really quite rare, and if I had to guess, I'd say 50% or
even 75% of EVERYTHING in the US was built in the 1970s or later.

- Logan
  #54   Report Post  
Logan Shaw
 
Posts: n/a
Default

Pooh Bear wrote:
Snowdog wrote:
There is no grounding wire. I do see a ground terminal on the outlet to add
a ground wire. House was built in '56.


Is that legal ?

Certainly wouldn't be in the UK.

Are ungrounded outlets common in the US ?


On older houses (say, 1960s or before, or maybe it's 1950s or before),
yes they are common, but not on newer construction.

Keep in mind that, in the US, virtually everything is "new construction"
by UK standards. We do have the occasional house that is over 100 years
old, but it's really quite rare, and if I had to guess, I'd say 50% or
even 75% of EVERYTHING in the US was built in the 1970s or later.

- Logan
  #55   Report Post  
Logan Shaw
 
Posts: n/a
Default

Pooh Bear wrote:
Snowdog wrote:
There is no grounding wire. I do see a ground terminal on the outlet to add
a ground wire. House was built in '56.


Is that legal ?

Certainly wouldn't be in the UK.

Are ungrounded outlets common in the US ?


On older houses (say, 1960s or before, or maybe it's 1950s or before),
yes they are common, but not on newer construction.

Keep in mind that, in the US, virtually everything is "new construction"
by UK standards. We do have the occasional house that is over 100 years
old, but it's really quite rare, and if I had to guess, I'd say 50% or
even 75% of EVERYTHING in the US was built in the 1970s or later.

- Logan


  #56   Report Post  
Phil Allison
 
Posts: n/a
Default


"Snowdog"
Thanks to everyone for your helpful comments. Quick recap..bass player

gets
shocked on the lips by vocal mic while wearing his bass.

I pulled the three prong outlet from the wall that the bass player plugs
into...and sure enough, there are only two wires connected to the plug.
There is no grounding wire. I do see a ground terminal on the outlet to

add
a ground wire. House was built in '56.

What are my options to add a ground?



**

Step 1. Buy an extension lead and plug it into an earthed outlet.

Step 2. Buy a multi outlet power adaptor - if possible one with a GFI
included.

Step 3. Have all the instrument amps plug into it.

Step 4. Plug the adaptor board into the extension lead.




............. Phil



  #57   Report Post  
Phil Allison
 
Posts: n/a
Default


"Snowdog"
Thanks to everyone for your helpful comments. Quick recap..bass player

gets
shocked on the lips by vocal mic while wearing his bass.

I pulled the three prong outlet from the wall that the bass player plugs
into...and sure enough, there are only two wires connected to the plug.
There is no grounding wire. I do see a ground terminal on the outlet to

add
a ground wire. House was built in '56.

What are my options to add a ground?



**

Step 1. Buy an extension lead and plug it into an earthed outlet.

Step 2. Buy a multi outlet power adaptor - if possible one with a GFI
included.

Step 3. Have all the instrument amps plug into it.

Step 4. Plug the adaptor board into the extension lead.




............. Phil



  #58   Report Post  
Phil Allison
 
Posts: n/a
Default


"Snowdog"
Thanks to everyone for your helpful comments. Quick recap..bass player

gets
shocked on the lips by vocal mic while wearing his bass.

I pulled the three prong outlet from the wall that the bass player plugs
into...and sure enough, there are only two wires connected to the plug.
There is no grounding wire. I do see a ground terminal on the outlet to

add
a ground wire. House was built in '56.

What are my options to add a ground?



**

Step 1. Buy an extension lead and plug it into an earthed outlet.

Step 2. Buy a multi outlet power adaptor - if possible one with a GFI
included.

Step 3. Have all the instrument amps plug into it.

Step 4. Plug the adaptor board into the extension lead.




............. Phil



  #59   Report Post  
Ty Ford
 
Posts: n/a
Default

On Fri, 24 Sep 2004 17:17:04 -0400, Stu Venable wrote
(in article et):

"George" wrote in message
...
In article lH%4d.359927$8_6.120251@attbi_s04,
"Tony Briggs" wrote:

I hardly think it is illegal.

Probably 50 % of homes built before WW2 probably have an ungrounded

outlet
in every room....


I don't think you can sell a house in my local with outdated wiring
George


I bought my house about 6 years ago (in Southern Calif.), nearly all of my
outlets were two-prong, with no ground. Only in the kitchen and bathrooms
did I have grounds, and they were GFCIs with the ground wires looped around
to "fool" them from shutting off.

Stu


I have a mixture of 2 and 3 here. We bought this 1954 rancher 7 years ago.

Also be aware that the wiring may have been incorrectly installed. Just cause
it's in the walls, don't mean it's right.

As mentioned earlier, be careful, YOU COULD DIE FROM THIS!

Ty Ford



-- Ty Ford's equipment reviews, audio samples, rates and other audiocentric
stuff are at www.tyford.com

  #60   Report Post  
Ty Ford
 
Posts: n/a
Default

On Fri, 24 Sep 2004 17:17:04 -0400, Stu Venable wrote
(in article et):

"George" wrote in message
...
In article lH%4d.359927$8_6.120251@attbi_s04,
"Tony Briggs" wrote:

I hardly think it is illegal.

Probably 50 % of homes built before WW2 probably have an ungrounded

outlet
in every room....


I don't think you can sell a house in my local with outdated wiring
George


I bought my house about 6 years ago (in Southern Calif.), nearly all of my
outlets were two-prong, with no ground. Only in the kitchen and bathrooms
did I have grounds, and they were GFCIs with the ground wires looped around
to "fool" them from shutting off.

Stu


I have a mixture of 2 and 3 here. We bought this 1954 rancher 7 years ago.

Also be aware that the wiring may have been incorrectly installed. Just cause
it's in the walls, don't mean it's right.

As mentioned earlier, be careful, YOU COULD DIE FROM THIS!

Ty Ford



-- Ty Ford's equipment reviews, audio samples, rates and other audiocentric
stuff are at www.tyford.com



  #61   Report Post  
Ty Ford
 
Posts: n/a
Default

On Fri, 24 Sep 2004 23:56:01 -0400, Pooh Bear wrote
(in article ):



Snowdog wrote:

I pulled the three prong outlet from the wall that the bass player plugs
into...and sure enough, there are only two wires connected to the plug.
There is no grounding wire. I do see a ground terminal on the outlet to add
a ground wire. House was built in '56.


Is that legal ?

Certainly wouldn't be in the UK.

Are ungrounded outlets common in the US ?


Graham


Graham,

As I mentioned earlier, my 1956 house is a mix of 2 and 3. If something
buzzed in a two, we just replugged it 180 degrees to solve the problem.

There are also polarized 2-prong plugs (one blade is larger than the other)
that can only be plugged in ONE WAY. If the wiring scheme is proper, the
ground and neutral are the same all the way back to the panel.
(Unfortunately, sometimes they get flipped)

Maybe someone else can pipe in here. I'm at the edge of my correct info
border on this specific point.

Regards,

Ty Ford



-- Ty Ford's equipment reviews, audio samples, rates and other audiocentric
stuff are at www.tyford.com

  #62   Report Post  
Ty Ford
 
Posts: n/a
Default

On Fri, 24 Sep 2004 23:56:01 -0400, Pooh Bear wrote
(in article ):



Snowdog wrote:

I pulled the three prong outlet from the wall that the bass player plugs
into...and sure enough, there are only two wires connected to the plug.
There is no grounding wire. I do see a ground terminal on the outlet to add
a ground wire. House was built in '56.


Is that legal ?

Certainly wouldn't be in the UK.

Are ungrounded outlets common in the US ?


Graham


Graham,

As I mentioned earlier, my 1956 house is a mix of 2 and 3. If something
buzzed in a two, we just replugged it 180 degrees to solve the problem.

There are also polarized 2-prong plugs (one blade is larger than the other)
that can only be plugged in ONE WAY. If the wiring scheme is proper, the
ground and neutral are the same all the way back to the panel.
(Unfortunately, sometimes they get flipped)

Maybe someone else can pipe in here. I'm at the edge of my correct info
border on this specific point.

Regards,

Ty Ford



-- Ty Ford's equipment reviews, audio samples, rates and other audiocentric
stuff are at www.tyford.com

  #63   Report Post  
Phil Allison
 
Posts: n/a
Default


"Ty Ford" = Typhoid

Pooh Bear


Are ungrounded outlets common in the US ?


As I mentioned earlier, my 1956 house is a mix of 2 and 3. If something
buzzed in a two, we just replugged it 180 degrees to solve the problem.


** Only possible if you are still alive to do it.


There are also polarized 2-prong plugs (one blade is larger than the

other)
that can only be plugged in ONE WAY. If the wiring scheme is proper, the
ground and neutral are the same all the way back to the panel.



** Only one of those wires carries the AC current while the other does
NOT.


(Unfortunately, sometimes they get flipped)



** Errr - that is why an independent third wire is a good idea.


Maybe someone else can pipe in here. I'm at the edge of my correct info
border on this specific point.



** ROTFLMAO !!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!


Typhoid is over the border's edge of sanity with all his putrid posts.





.............. Phil




  #64   Report Post  
Phil Allison
 
Posts: n/a
Default


"Ty Ford" = Typhoid

Pooh Bear


Are ungrounded outlets common in the US ?


As I mentioned earlier, my 1956 house is a mix of 2 and 3. If something
buzzed in a two, we just replugged it 180 degrees to solve the problem.


** Only possible if you are still alive to do it.


There are also polarized 2-prong plugs (one blade is larger than the

other)
that can only be plugged in ONE WAY. If the wiring scheme is proper, the
ground and neutral are the same all the way back to the panel.



** Only one of those wires carries the AC current while the other does
NOT.


(Unfortunately, sometimes they get flipped)



** Errr - that is why an independent third wire is a good idea.


Maybe someone else can pipe in here. I'm at the edge of my correct info
border on this specific point.



** ROTFLMAO !!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!


Typhoid is over the border's edge of sanity with all his putrid posts.





.............. Phil




  #65   Report Post  
ScotFraser
 
Posts: n/a
Default

If the wiring scheme is proper, the
ground and neutral are the same all the way back to the panel. BRBR

A small clarification: the ground & neutral are separate wires, but are tied
together at the service panel.
Scott Fraser


  #66   Report Post  
ScotFraser
 
Posts: n/a
Default

If the wiring scheme is proper, the
ground and neutral are the same all the way back to the panel. BRBR

A small clarification: the ground & neutral are separate wires, but are tied
together at the service panel.
Scott Fraser
  #67   Report Post  
Ed Anson
 
Posts: n/a
Default

Logan Shaw wrote:
George wrote:


From what I understand the two prong outlets were grounded through the
armored jacket or conduit
so if a ground path is in place through one of thes methods then simply
bond the green screw of the three hole edison connector to the metal job
box



I think the OP said the wire was two conductor enclosed in a mesh
that did not appear to be metal. So, apparently there really is
no separate ground.


Right. I have wiring like that in my house. My electrician calls it
"knob and tube" wiring. That's because it consists (inside the walls) of
pairs of wires several inches apart that are supported by knobs and
protected by tubes when passing through studs. It has a cloth-like layer
of insulation. Where it passes into the electrical box, there is usually
an additional layer of insulation, presumably for mechanical protection
against abrasion.

AFAIK this was the standard form of wiring until sometime in the late
50's or early 60's when Romex took over.

Although it is no longer up to code, it is perfectly safe if properly
maintained. Its only drawback is the lack of a ground line. That's why I
have added modern circuits where I use electronics.

  #68   Report Post  
Ed Anson
 
Posts: n/a
Default

Logan Shaw wrote:
George wrote:


From what I understand the two prong outlets were grounded through the
armored jacket or conduit
so if a ground path is in place through one of thes methods then simply
bond the green screw of the three hole edison connector to the metal job
box



I think the OP said the wire was two conductor enclosed in a mesh
that did not appear to be metal. So, apparently there really is
no separate ground.


Right. I have wiring like that in my house. My electrician calls it
"knob and tube" wiring. That's because it consists (inside the walls) of
pairs of wires several inches apart that are supported by knobs and
protected by tubes when passing through studs. It has a cloth-like layer
of insulation. Where it passes into the electrical box, there is usually
an additional layer of insulation, presumably for mechanical protection
against abrasion.

AFAIK this was the standard form of wiring until sometime in the late
50's or early 60's when Romex took over.

Although it is no longer up to code, it is perfectly safe if properly
maintained. Its only drawback is the lack of a ground line. That's why I
have added modern circuits where I use electronics.

  #69   Report Post  
Mike Rivers
 
Posts: n/a
Default


In article writes:

As I mentioned earlier, my 1956 house is a mix of 2 and 3. If something
buzzed in a two, we just replugged it 180 degrees to solve the problem.


** Only possible if you are still alive to do it.


And only dangerous if one side of the power line is tied to something
in the box that you can touch.

There are also polarized 2-prong plugs (one blade is larger than the

other)
that can only be plugged in ONE WAY. If the wiring scheme is proper, the
ground and neutral are the same all the way back to the panel.



** Only one of those wires carries the AC current while the other does
NOT.


Phil, Phyl, Chlorophyll, must we go through this again? If there's
something plugged into the outlet that's turned on and working, both
wires carry the AC current. It's a circuit. Have a beer, relax, and
come back when you have a clearer head.

(Unfortunately, sometimes they get flipped)

** Errr - that is why an independent third wire is a good idea.


Not in this country. The safety ground (unless they have a different
"third wire" in your country) is there to assure that if a short
circuit develops between the hot side of the line and the case, it
will find a return path through a lower impedance than someone who
touches it who's grounded. This isn't intended to protect against
miswiring or stupid construction, it's designed to provide a degree of
safety if something fails, like insulation, or a line bypass capacitor
(if anyone still does that). While it may result in a tripped circuit
breaker if the hot side of a plug is connected to the chassis due to
miswiring, that isn't the purpose of the safety ground.


--
I'm really Mike Rivers )
However, until the spam goes away or Hell freezes over,
lots of IP addresses are blocked from this system. If
you e-mail me and it bounces, use your secret decoder ring
and reach me he double-m-eleven-double-zero at yahoo
  #70   Report Post  
Mike Rivers
 
Posts: n/a
Default


In article writes:

As I mentioned earlier, my 1956 house is a mix of 2 and 3. If something
buzzed in a two, we just replugged it 180 degrees to solve the problem.


** Only possible if you are still alive to do it.


And only dangerous if one side of the power line is tied to something
in the box that you can touch.

There are also polarized 2-prong plugs (one blade is larger than the

other)
that can only be plugged in ONE WAY. If the wiring scheme is proper, the
ground and neutral are the same all the way back to the panel.



** Only one of those wires carries the AC current while the other does
NOT.


Phil, Phyl, Chlorophyll, must we go through this again? If there's
something plugged into the outlet that's turned on and working, both
wires carry the AC current. It's a circuit. Have a beer, relax, and
come back when you have a clearer head.

(Unfortunately, sometimes they get flipped)

** Errr - that is why an independent third wire is a good idea.


Not in this country. The safety ground (unless they have a different
"third wire" in your country) is there to assure that if a short
circuit develops between the hot side of the line and the case, it
will find a return path through a lower impedance than someone who
touches it who's grounded. This isn't intended to protect against
miswiring or stupid construction, it's designed to provide a degree of
safety if something fails, like insulation, or a line bypass capacitor
(if anyone still does that). While it may result in a tripped circuit
breaker if the hot side of a plug is connected to the chassis due to
miswiring, that isn't the purpose of the safety ground.


--
I'm really Mike Rivers )
However, until the spam goes away or Hell freezes over,
lots of IP addresses are blocked from this system. If
you e-mail me and it bounces, use your secret decoder ring
and reach me he double-m-eleven-double-zero at yahoo


  #71   Report Post  
Scott Dorsey
 
Posts: n/a
Default

Pooh Bear wrote:
Snowdog wrote:

I pulled the three prong outlet from the wall that the bass player plugs
into...and sure enough, there are only two wires connected to the plug.
There is no grounding wire. I do see a ground terminal on the outlet to add
a ground wire. House was built in '56.


Is that legal ?


No, not even a little bit. That's the sort of thing that insurance companies
like to point at when they decide not to pay on a claim, too.

Certainly wouldn't be in the UK.

Are ungrounded outlets common in the US ?


They are very common in older construction, but it is VERY illegal to put
a three-prong outlet up without a ground connected. Older construction with
two-prong outlets is common, though. The one cheat around this is that if
a GFI is used, a three-prong outlet can be installed because the GFI
protects against ground leakage by shutting the circuit off if it detects
any imbalance.
--scott

--
"C'est un Nagra. C'est suisse, et tres, tres precis."
  #72   Report Post  
Scott Dorsey
 
Posts: n/a
Default

Pooh Bear wrote:
Snowdog wrote:

I pulled the three prong outlet from the wall that the bass player plugs
into...and sure enough, there are only two wires connected to the plug.
There is no grounding wire. I do see a ground terminal on the outlet to add
a ground wire. House was built in '56.


Is that legal ?


No, not even a little bit. That's the sort of thing that insurance companies
like to point at when they decide not to pay on a claim, too.

Certainly wouldn't be in the UK.

Are ungrounded outlets common in the US ?


They are very common in older construction, but it is VERY illegal to put
a three-prong outlet up without a ground connected. Older construction with
two-prong outlets is common, though. The one cheat around this is that if
a GFI is used, a three-prong outlet can be installed because the GFI
protects against ground leakage by shutting the circuit off if it detects
any imbalance.
--scott

--
"C'est un Nagra. C'est suisse, et tres, tres precis."
  #73   Report Post  
Pooh Bear
 
Posts: n/a
Default

Logan Shaw wrote:

Pooh Bear wrote:
Snowdog wrote:
There is no grounding wire. I do see a ground terminal on the outlet to add
a ground wire. House was built in '56.


Is that legal ?

Certainly wouldn't be in the UK.

Are ungrounded outlets common in the US ?


On older houses (say, 1960s or before, or maybe it's 1950s or before),
yes they are common, but not on newer construction.


But they ought to be 2 pin sockets - right ?

I can remember that the new build UK house my family moved into in 1956 had
grounded 3 pole sockets ( but still the older 5/15Amp 'round pin' type - still
used in India - and most likely elsewhere too - before we went to rectangular pin
with internal fusing ). The round pin sockets date back to the 30s or 40s at a
guess.

Keep in mind that, in the US, virtually everything is "new construction"
by UK standards. We do have the occasional house that is over 100 years
old, but it's really quite rare, and if I had to guess, I'd say 50% or
even 75% of EVERYTHING in the US was built in the 1970s or later.


My own house is 112 yrs old. Obviously it had no electricity to begin with. The
evidence suggest that it was originally wired maybe in the 30s or 40s and
rewired probably in the 60s . Both types of cable ( remnants of the old rubber
insulated type and the new PVC insulated ) are 3 core.


Graham

  #74   Report Post  
Pooh Bear
 
Posts: n/a
Default

Logan Shaw wrote:

Pooh Bear wrote:
Snowdog wrote:
There is no grounding wire. I do see a ground terminal on the outlet to add
a ground wire. House was built in '56.


Is that legal ?

Certainly wouldn't be in the UK.

Are ungrounded outlets common in the US ?


On older houses (say, 1960s or before, or maybe it's 1950s or before),
yes they are common, but not on newer construction.


But they ought to be 2 pin sockets - right ?

I can remember that the new build UK house my family moved into in 1956 had
grounded 3 pole sockets ( but still the older 5/15Amp 'round pin' type - still
used in India - and most likely elsewhere too - before we went to rectangular pin
with internal fusing ). The round pin sockets date back to the 30s or 40s at a
guess.

Keep in mind that, in the US, virtually everything is "new construction"
by UK standards. We do have the occasional house that is over 100 years
old, but it's really quite rare, and if I had to guess, I'd say 50% or
even 75% of EVERYTHING in the US was built in the 1970s or later.


My own house is 112 yrs old. Obviously it had no electricity to begin with. The
evidence suggest that it was originally wired maybe in the 30s or 40s and
rewired probably in the 60s . Both types of cable ( remnants of the old rubber
insulated type and the new PVC insulated ) are 3 core.


Graham

  #75   Report Post  
Pooh Bear
 
Posts: n/a
Default


Scott Dorsey wrote:

Pooh Bear wrote:
Snowdog wrote:

I pulled the three prong outlet from the wall that the bass player plugs
into...and sure enough, there are only two wires connected to the plug.
There is no grounding wire. I do see a ground terminal on the outlet to add
a ground wire. House was built in '56.


Is that legal ?


No, not even a little bit. That's the sort of thing that insurance companies
like to point at when they decide not to pay on a claim, too.


I'll bet they do !


Certainly wouldn't be in the UK.

Are ungrounded outlets common in the US ?


They are very common in older construction, but it is VERY illegal to put
a three-prong outlet up without a ground connected.


I suspected as much. So the ungrounded 3 pin outlets are most likely installed by
a previous owner with no sense ?


Older construction with
two-prong outlets is common, though. The one cheat around this is that if
a GFI is used, a three-prong outlet can be installed because the GFI
protects against ground leakage by shutting the circuit off if it detects
any imbalance.


As in a GFI at the 'panel' ( commonly referred to as the 'fusebox' in the UK
although it normally contains a mixture of MCBs and RCDs these days ). Mine
actually only has good old fashioned fuses but it's an older house ;-)

MCB = miniature circuit breaker ( fuse replacement )
RCD = residual current device aka. ELCB ( earth leakage current breaker ) or GFI (
US terminology ground fault interruptor ).


Graham






  #76   Report Post  
Pooh Bear
 
Posts: n/a
Default


Scott Dorsey wrote:

Pooh Bear wrote:
Snowdog wrote:

I pulled the three prong outlet from the wall that the bass player plugs
into...and sure enough, there are only two wires connected to the plug.
There is no grounding wire. I do see a ground terminal on the outlet to add
a ground wire. House was built in '56.


Is that legal ?


No, not even a little bit. That's the sort of thing that insurance companies
like to point at when they decide not to pay on a claim, too.


I'll bet they do !


Certainly wouldn't be in the UK.

Are ungrounded outlets common in the US ?


They are very common in older construction, but it is VERY illegal to put
a three-prong outlet up without a ground connected.


I suspected as much. So the ungrounded 3 pin outlets are most likely installed by
a previous owner with no sense ?


Older construction with
two-prong outlets is common, though. The one cheat around this is that if
a GFI is used, a three-prong outlet can be installed because the GFI
protects against ground leakage by shutting the circuit off if it detects
any imbalance.


As in a GFI at the 'panel' ( commonly referred to as the 'fusebox' in the UK
although it normally contains a mixture of MCBs and RCDs these days ). Mine
actually only has good old fashioned fuses but it's an older house ;-)

MCB = miniature circuit breaker ( fuse replacement )
RCD = residual current device aka. ELCB ( earth leakage current breaker ) or GFI (
US terminology ground fault interruptor ).


Graham




  #77   Report Post  
Pooh Bear
 
Posts: n/a
Default



ScotFraser wrote:

If the wiring scheme is proper, the
ground and neutral are the same all the way back to the panel. BRBR

A small clarification: the ground & neutral are separate wires, but are tied
together at the service panel.


In the UK, the ground conductor is only connected to neutral at the relevant
'sub-station' - the local transformer supplying the district.

Grounds are commonly additionally tied or 'strapped' to copper pipes carrying
the water supply. Called multiple protective ground earthing IIRC.


Graham

  #78   Report Post  
Pooh Bear
 
Posts: n/a
Default



ScotFraser wrote:

If the wiring scheme is proper, the
ground and neutral are the same all the way back to the panel. BRBR

A small clarification: the ground & neutral are separate wires, but are tied
together at the service panel.


In the UK, the ground conductor is only connected to neutral at the relevant
'sub-station' - the local transformer supplying the district.

Grounds are commonly additionally tied or 'strapped' to copper pipes carrying
the water supply. Called multiple protective ground earthing IIRC.


Graham

  #79   Report Post  
Phil Allison
 
Posts: n/a
Default


"Mike Rivers"
Phil Allison

As I mentioned earlier, my 1956 house is a mix of 2 and 3. If

something
buzzed in a two, we just replugged it 180 degrees to solve the

problem.


** Only possible if you are still alive to do it.


And only dangerous if one side of the power line is tied to something
in the box that you can touch.


** Just what a "polarity cap" in fact does.



There are also polarized 2-prong plugs (one blade is larger than the

other) that can only be plugged in ONE WAY. If the wiring scheme is

proper, the
ground and neutral are the same all the way back to the panel.



** Only one of those wires carries the AC current while the other does
NOT.



Phil, Phyl, Chlorophyll, must we go through this again? If there's
something plugged into the outlet that's turned on and working, both
wires carry the AC current. It's a circuit. Have a beer, relax, and
come back when you have a clearer head.



** Learn to read you stinking, Parrott moron .

The two wires are the "ground" and "neutral" conductors.



(Unfortunately, sometimes they get flipped)


** Errr - that is why an independent third wire is a good idea.


Not in this country.



** **** off you brain dead Parrott.



The safety ground (unless they have a different
"third wire" in your country) is there to assure that if a short
circuit develops between the hot side of the line and the case, it
will find a return path through a lower impedance than someone who
touches it who's grounded.



** That is WHY it must be a third, independent conductor - not one of
the two wires carrying AC current that MIGHT get flipped.

The neutral wire CANNOT be used as a safety ground, even though it is at
ground potential at the wall outlet.



............. Phil



  #80   Report Post  
Phil Allison
 
Posts: n/a
Default


"Mike Rivers"
Phil Allison

As I mentioned earlier, my 1956 house is a mix of 2 and 3. If

something
buzzed in a two, we just replugged it 180 degrees to solve the

problem.


** Only possible if you are still alive to do it.


And only dangerous if one side of the power line is tied to something
in the box that you can touch.


** Just what a "polarity cap" in fact does.



There are also polarized 2-prong plugs (one blade is larger than the

other) that can only be plugged in ONE WAY. If the wiring scheme is

proper, the
ground and neutral are the same all the way back to the panel.



** Only one of those wires carries the AC current while the other does
NOT.



Phil, Phyl, Chlorophyll, must we go through this again? If there's
something plugged into the outlet that's turned on and working, both
wires carry the AC current. It's a circuit. Have a beer, relax, and
come back when you have a clearer head.



** Learn to read you stinking, Parrott moron .

The two wires are the "ground" and "neutral" conductors.



(Unfortunately, sometimes they get flipped)


** Errr - that is why an independent third wire is a good idea.


Not in this country.



** **** off you brain dead Parrott.



The safety ground (unless they have a different
"third wire" in your country) is there to assure that if a short
circuit develops between the hot side of the line and the case, it
will find a return path through a lower impedance than someone who
touches it who's grounded.



** That is WHY it must be a third, independent conductor - not one of
the two wires carrying AC current that MIGHT get flipped.

The neutral wire CANNOT be used as a safety ground, even though it is at
ground potential at the wall outlet.



............. Phil



Reply
Thread Tools
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
What are they Teaching Michael McKelvy Audio Opinions 199 October 15th 04 07:56 PM
selecting a live vocal mic db:southcongress Pro Audio 34 October 20th 03 05:46 AM
Live Sound Vs Studio Sound FrankDebro1 Pro Audio 155 October 10th 03 06:35 PM
help with creating Izotope vinyl vocal effect live. Anthony Pro Audio 3 September 4th 03 04:10 AM


All times are GMT +1. The time now is 03:39 AM.

Powered by: vBulletin
Copyright ©2000 - 2025, Jelsoft Enterprises Ltd.
Copyright ©2004-2025 AudioBanter.com.
The comments are property of their posters.
 

About Us

"It's about Audio and hi-fi"